lets start here
Additional standard ampere ratings for fuses shall be 1, 3, 6, 10, and 601.
would you agree that 10 amps is a standard OC protection device
As kwired already pointed out, the smallest standard circuit breaker size is 15. If we're protecting the circuit with a circuit breaker OCPD, then we don't need to provide protection smaller than 15A.
210.23 (A) 15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2)
It doesn?t say a 15 amp rated branch circuit.
It does say 15 and 20 amp branch circuits
210.23(A) says a 15amp branch circuit
OR a 20amp branch circuit shall be permitted to supply lighting units. In this case, we are using a 15amp branch circuit to supply lighting units, so we meet 210.23(A).
I see a 15 amp branch circuits as one having 15 amp over- current protection and conductors with an ampacity in accordance with table 310.16..
The end result would mean a 15 amp branch circuit would need a conductor with adjusted 20 amp capacity table 310.16
I don't follow you're logic here. 210.23(A) doesn't say anything about conductor size. 210.19(A)(1) says branch circuit conductors shall have an ampacity not less than the load to be served. We are meeting that requirement.
Unless it under supervised engineering
I do not see where the table ampacities are allowed to be reduced.
I do see where the ampacities in these tables have to be maintained by adjusting the conductor sizes.
Not only are the ampacities in T310.16 "allowed" to be reduced, but they are required to be reduced in specific instances (not under supervised engineering.)
310.15(B) says "Ampacities for conductors rated 0 to 2000 volts shall be as specified in the Allowable Ampacity Tables 310.16 thru 310.19...
as modified by (B)(1) thru (B)(6).
310.15(B)(2) says "Where the number of current-carrying conductors in a raceway or cable exceeds three...the allowable ampacity of each conductor
shall be reduced as shown in T310.15(B)(2)(a)." (These section numbers are based on 2008 NEC, I think they have changed in 2011).