...In cases of critical power delivery, like in data centers, the tie-breaker is often Normally-closed, so that if one of the transformers fails, or if a main breaker trips, there will be no power interruption since all of the load will be supplied through the other transformer.
But, this parallel operation results in twice the amount of fault current on the secondary bus, so systems designed to operate with the Tie-breaker closed must have twice the fault current rating for the distribution gear as compared to a system where the breakers are interlocked such that the secondaries can never be paralleled..