Hello all. I have a technical question regarding an installation. In a single-family dwelling I found the following: a branch circuit connected to two different breakers in the interior sub-panel. Both breakers are on the same phase and are both 15 amp. There is a #14 connected to each of the two which then connect to a third #14 under a wire nut. This third conductor is the load wire to the branch circuit itself.
..............................a or b phase.....................................
/ \
/ \
/ \
cb1---------------------------------0-----------------------------------------------------cb2
15a \ 15a
\
\...............................to branch circuit
The person that did this is trying to convince me that this would allow 30 amps of overcurrent protection, but I believe it's still 15. Either way I'm going to disconnect the circuit from one of the breakers, as the installation is dangerous in my opinion, especially for anyone working on it. I was just wondering how the breakers would operate, or fail to correctly, in relation to the branch circuit. Thanks for your help, gm
..............................a or b phase.....................................
/ \
/ \
/ \
cb1---------------------------------0-----------------------------------------------------cb2
15a \ 15a
\
\...............................to branch circuit
The person that did this is trying to convince me that this would allow 30 amps of overcurrent protection, but I believe it's still 15. Either way I'm going to disconnect the circuit from one of the breakers, as the installation is dangerous in my opinion, especially for anyone working on it. I was just wondering how the breakers would operate, or fail to correctly, in relation to the branch circuit. Thanks for your help, gm