mc5w said:Most elevator branch circuits must originate at 1 or more panelboards located INSIDE the machine room. This is both to make the branch circuits easier to locate and to prevent accidental disconnection of lighting and sump pump circuits and so forth.
The problem gets to be when you only need 3 120 volt branch circuits off of a 120Y208 volt system and the main motor runs on a single 480 volts branch circuit. Theoretically, the circuit breakers or fuses outside of the machine room would need to be 200% of the circuit breakers fuses inside of the machine room so that the external overcurrent devices count as feeder devices and so that the devices inside of the machine room trip or blow first.
Feeder breakers and fusible switches outside of the machine room need to be locked ON so as to avoid accidental disconnection.
A lot of architects and engineers get this one wrong when drawing plans for a building that has only 1 elevator. The requirement for 1 or more subpanels in an elevator machine room is poorly written as a bunch of branch circuit rules - not quite so smart C average people have a hard time realizing this because of poor writing of NEC 620.23 through 620.25.
Mike Cole
Bkaz, did you look at page 2? Don suggested fuses, Jim T suggested that you not worry about it.bkaz said:Can anyone offer any suggestions to my post on this thread dated 11/10/06. I realize I jumped in the middle of the thread.
Steve-o!milwaukeesteve said:Also, Fusing is not Ground Fault Protection. Fuses act as OverCurrent Protection and Short Circuit Protection. They do NOT sense Faults to ground. Yes, they will or may trip as a result of a fault, only because the resulting current due to the fault may trip the overCurrent Protection, but it is not Fault protection.