In what circumstances we do need two ground rods six feet apart at tbe service?
In what circumstances we do need two ground rods six feet apart at tbe service?
Hi
In what circumstances we do need two ground rods six feet apart at tbe service?
Unless you can prove 25 ohms or less resistance, then you have to drive two rods. That is unless you have a UFFER or other electrode.
That is, another electrode other than a pipe, plate, or underground waterpipe.With those, as I read it, you need to prove the second made electrode in not needed, or supplement the first.
What I meant was you may not have to drive the 2nd rod if you have another electrode to connect to. Of course if you have a UFFER, it is not required to have supplementry electrodes. I should have left out the UFFER from my reply to the OP.
I was trying to agree with you.
Just clarifying the 'other electrodes' you mentioned.![]()