double tap breaker

Status
Not open for further replies.

shelco

Senior Member
Can you legally connect 2 conductors on a breaker?
Specifically a Sq D 20amp. this has a pressure plate with what what looks like a spot for a conductor on either side. Conductors would be the same size.

[ November 30, 2005, 08:12 AM: Message edited by: shelco ]
 
Re: double tap breaker

Generally no. Specifically, that Square D yes. Look at the side of the breaker for the wire size and combination information.
 
Re: double tap breaker

It should be listyed on the breaker. Generally for the one you mentioned it can accept two.
 
Re: double tap breaker

I would agree that SQ D will accept 2 conductors. But if the info isn't readily available or, when in doubt, you could simply splice the two conductors together and pigtail a short single conductor to the breaker.
 
Re: double tap breaker

I agree with Jim. There is a little image embossed on the SqD breakers that allows 2 # 14 thru #10.
 