Stevenfyeager
Senior Member
- Location
- United States, Indiana
- Occupation
- electrical contractor
Home inspection shows double tapping in panel, on (3) 2 pole breakers. Panel is full, I recommended to the realtor that a sub panel needs to be installed. She wrote back saying an electrician told her you can just wire nut pig tail them in the panel. While I have heard that is acceptable for single pole circuits, I told her that since all 3 double taps are on 2 pole breakers, overloading would still be the issue. Did I tell her correctly ?