Minuteman
 - The Sooner Nation
Customer calls me about his electric bill being real high. His Hot Tub store is in the east half of a building. There was only one meter, but someone moved into the west half in November. They separated the wiring and added a meter, making it Suite B.
His electric bill from November and December are almost 3 times that of the last 3 years for the same 2 months. He called the PoCo, and they told him to have an electrician meet their service guy there.
When we opened the CT can, this is what we found.
(The neutral and the CT wiring are left out for clarity)
Power comes into the CT can from the bottom, through the CT's, to a block connector. One conductor leaves the block connector and goes to the Suit A conduit. The other conductor leaves the block and goes back through the CT and to the conduit for Suite B's meter.
If the Suite B conductors went through the CT in the opposing direction, the fields would cancel and on to the B meter with no problem. However, since the conductors are travel the way they do, the CT re-reads the current and is re-recorded on Suite A's meter. The PoCo service guy agreed, and was to come back after the store closes tonight to make the change.
My question. Would the effect of all this actually give PoCo triple billing for the usage of Suite B? Once for the recording on the standard type meter for Suite B. Twice for the doubling effect of going through Suite A's CT meter?
CORRECTION: I just noticed that I drew the Suite B blue conductor wrong. It also leaves the block and goes through the Ct from the left to the right. Not as shown.