A home inspector says having two #12 neutral wires under one screw on the grounding bar in the panel is not allowed. Is he right? Thanks.
Ground bar and Neutral bar are joined from the inspector's photo. My instructor told us years ago that as long as the two wires are the same size, it is allowed. But I don't recall an NEC reference. I will check the panel brand when I look at the house today. Thank you.First of all, if there are separate grounding and neutral buses, you're using the wrong bus.
Otherwise, unless allowed by the panel maker, he is correct.
First of all, if there are separate grounding and neutral buses, you're using the wrong bus.
Otherwise, unless allowed by the panel maker, he is correct.
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individ
ual terminal that is not also used for another conductor.
My continuing Ed instructor years ago told us it is allowed only if the two wires are the same gauge. I don't think he referenced the NEC. Most of the older homes all have this, but what puzzles me is that no other home inspector I've been asked to follow has ever said this is a code violation. And I have been asked to address many home inspections. It's a first for me to see this tagged. I guess I could add an extra ground bar but I'd like to know if he is right.
Just to clarify what others have already posted, if the HI cited the problem in a MBP the grounds and neutrals are landed on the same ground/neutral bar. The reason you don’t land 2 neutrals under the same screw is because the likelihood that the screw can loosen from vibration or expansion/contraction over time is greater than you might think. If that happens it will begin to arc and could cause the insulation to melt and the loads (like lighting) to flicker. Having 2 EGC’s under one screw doesn’t present that specific problem (but may present others). If you’re in a MLP the neutrals and EGC’s are landed on a separate bar but again, the neutrals shouldn’t be terminated under the same screw for the reason cited.A home inspector says having two #12 neutral wires under one screw on the grounding bar in the panel is not allowed. Is he right? Thanks.
I’ve seen many older panels where a neutral and it’s associated EGC were landed under the same screw because of limited ground bar space. The correct way that it should have been done would have been to land each neutral on its own screw and group thr EGC’s together on a separate bar or lug.
If there is a “rating” shown on the panel cover as to how many EGC’s can be landed under one screw then that’s what you should go by. If not then “grouping” them together and landing them under a lug is a far better option than doubling them up under one screw.When you write "group EGC's together", are you referring to twisting together as many as will fit in a given hole in the busbar? I've encountered plenty of those in old panels, and it's a real treat straightening all that out to replace the panel.
Could the same can be said for neutrals as well?You are permitted to join many EGCs and use a single pigtail, as long as it's as large as the largest joined EGC.
Could the same can be said for neutrals as well?
If there is a “rating” shown on the panel cover as to how many EGC’s can be landed under one screw then that’s what you should go by. If not then “grouping” them together and landing them under a lug is a far better option than doubling them up under one screw.
The other reason you do not land two neutrals on one screw is that to work on one circuit neutral you would also interrupt (at least temporarily) the neutral of the other circuit. Similar to the problem with the neutral of an MWBC, in that you would have to open both breakers.Just to clarify what others have already posted, if the HI cited the problem in a MBP the grounds and neutrals are landed on the same ground/neutral bar. The reason you don’t land 2 neutrals under the same screw is because the likelihood that the screw can loosen from vibration or expansion/contraction over time is greater than you might think. If that happens it will begin to arc and could cause the insulation to melt and the loads (like lighting) to flicker. Having 2 EGC’s under one screw doesn’t present that specific problem (but may present others). If you’re in a MLP the neutrals and EGC’s are landed on a separate bar but again, the neutrals shouldn’t be terminated under the same screw for the reason cited.
...
...
That’s correct and a good point. Should the neutral on a MWBC that has been doubled up become loose it will cause irreversible problems.:thumbsup:The other reason you do not land two neutrals on one screw is that to work on one circuit neutral you would also interrupt (at least temporarily) the neutral of the other circuit. Similar to the problem with the neutral of an MWBC, in that you would have to open both breakers.
Sent from my XT1585 using Tapatalk
When is that going to happen? Do you know something I don’t? AFAIK you are required to use a 2-p breaker as it stands right now.Of course the danger of sending 240 volts to 120 volt appliances will not exist in future wiring because multi-wire circuits will be prohibited in residential wiring. I consider this good practice and have not shared a residential neutral in 10 years.
Our AHJ does not allow twisting ground wires together in a panel, they must each connect to a terminal but can be doubled up if same wire gauge and permitted by panel specs. Individual landing of neutral conductors which i do, is a considered good practice but not enforced...they allow doubling up same as ground wire. I have never seen a panel with enough ground screw terminals, so I routinely add additional ground terminals... I connect the added terminal to existing terminal with a #6 jumper. Of course the danger of sending 240 volts to 120 volt appliances will not exist in future wiring because multi-wire circuits will be prohibited in residential wiring. I consider this good practice and have not shared a residential neutral in 10 years.