Have you ever though you understood something in the code pretty well, and then something comes along and you realize you don't understand it at all??
Augie's mention of a 60A breaker has me there now.
240.4 says you have to protect wire at it's ampacity. I don't see any exception for neutral wires.
So how can you have anything more than a 30 amp breaker protecting this #10 neutral wire?
Even worse, how can you ever reduce the size of a neutral wire?? 220.61 says we can reduce neutrals, but it doesn't give us any specific permission to ignore 240.4.
I'm confused.
And one more comment: 220.61 says we can reduce service and feeder neutral sizes. But I can't find anything that says we can reduce the neutral for a branch circuit.
It's not a branch circuit, it's the neutral for the feeders to a sub-panel. One of the books I looked at said that the 220v loads do not add anything to the neutral load so since there is only one 110v of 30 amps, the neutral only needs to be sized for that.
As far as knowing the code that's exactly what happened. I've just never seen it before and it actually threw me a little, so the more I read the more confused I got, until I read the Mcgraw-Hill book and then it made sense, I didn't like it any better, but it made sense.
Augie made me look some where that I hadn't looked before and I got the same answer, now of course if his breaker had been a 70 amp, the ungrounded conductors would still have been right, but the neutral would have been too small, but still could have been a #8. If I'm reading that section correctly.