Alwayslearningelec
- NJ
- Estimator
where I show orange lines in the photo
not because of gypsum, per se. just for support from steel framing regardless of ceiling finishIs it just because it’s in a gyp ceiling ?
I have, then drill holes in the grid and tie the emt down (and hanger wires)Would it require it if on a 2x2 acoustical ?
Is this a time consuming process to add fixture support bars or black iron?You can use short sections of black iron or fixture bars to support those fixtures.
Thanks. It's still hard for me to tell how these get applied.where I show orange lines in the photo
There are different positions for supports.
See the orange circles? There are round slots in the frame. Pick upper or lower 2 holes and run a 20-inch long or so 1/2 inch emt through, and rest it on top of the steel studs at the right height. Then 1-hole straps screwed down to secure them.Thanks. It's still hard for me to tell how these get applied.
I'm not sure. The archs don't seem to show which is unusual. Isn't that framing for an acoustical ceiling? My situation is a gyp board ceiling.What is the ceiling supported by T-bars or Chicago bar (hat channel)? Depending on what it is will determine how the fixture frame is set. This is a T-bar system. View attachment 2566598
But it is the same concept, only instead of the support bar resting over the T, you use self tapping screws and secure the bars to the vertical face of the studs.I'm not sure. The archs don't seem to show which is unusual. Isn't that framing for an acoustical ceiling? My situation is a gyp board ceiling.
That T-bar system is for a Sheetrock ceiling. If you Chicago bar you're fixture supports would sit on top of that.I'm not sure. The archs don't seem to show which is unusual. Isn't that framing for an acoustical ceiling? My situation is a gyp board ceiling.
You never answered the question as to what type of ceiling system they're using for the Sheetrock.So how would one know to order support bars with these? Now my vendor is sticking me with an extra charge to supply them and there's a lot.
Do you think they should've come with the fixture? THere's some info under "rough-in frame" section but I'm not clear on it.
Sorry. I looked thru the architectural and couldn’t find it . They always usually show it . I will check again tomorrow . Thank youYou never answered the question as to what type of ceiling system they're using for the Sheetrock.
Yeah, the answer may change based on what you're going to be attaching the bars to.Sorry. I looked thru the architectural and couldn’t find it . They always usually show it . I will check again tomorrow . Thank you
Thank you . So is it possible that the ceiling framing (as infinity referenced) could support the fixture or it’s 100% a support separate of that?From there site