Mustang125
Member
- Location
- New Hampshire
- Occupation
- Master Electrician, Project Manager and Estimator
Hello all, my customer is looking to VE the current design. the panel is shown as 600a but the calculated per phase KVA is:
A=58.41
B=54.41
C=49.03
for a total KVA of 161.85.
if i break this down to amps i believe i get the following:
A=162.13a
B=151.02a
C=136.09a
for a total of 449.25a
So theoretically couldn't we get away with a 200a panel? I'm going to suggest a 400a but I'm trying to understand the logic behind the math...
I apologize in advance as i do not do many design build jobs so this stuff gets rusty
A=58.41
B=54.41
C=49.03
for a total KVA of 161.85.
if i break this down to amps i believe i get the following:
A=162.13a
B=151.02a
C=136.09a
for a total of 449.25a
So theoretically couldn't we get away with a 200a panel? I'm going to suggest a 400a but I'm trying to understand the logic behind the math...
I apologize in advance as i do not do many design build jobs so this stuff gets rusty