OR58410 / (208/(sqr(3)) = 486
right answer
58410/120 = 486
Much less complicated
OR58410 / (208/(sqr(3)) = 486
right answer
I will provide a good thing to learn; there is a difference between 120/208V and 208Y/120V.
120/208 is a single phase 3W system derived from a 208Y/120V system, and
208Y/120V is a 3ph, 4W system.
That is true they are very often mistakenly used either way. There are a lot of engineers that use it incorrectly. I will say, prior to being an engineer, I was an electrician doing industrial work, and we made a lot of money on change orders every time they would put 120/208V on the drawings and we new they needed 208Y/120V.I never heard of that as those numbers, in reality are often used either way. I do remember someone saying something similar to this...
I have heard that differentiation before but I don't know if it's anything official.I never heard of that as those numbers, in reality are often used either way. I do remember someone saying something similar to this...
haha now you have me really confused. do you have a couple diagrams?I will provide a good thing to learn; there is a difference between 120/208V and 208Y/120V.
120/208 is a single phase 3W system derived from a 208Y/120V system, and
208Y/120V is a 3ph, 4W system.
I'm glad you asked.I have heard that differentiation before but I don't know if it's anything official.
Yes, indeed; but food for thought. Wouldn't this require a panel rated 800A; unless you can find a 600A, 100% rated breaker.OR
58410/120 = 486
Much less complicated
Why multiply the 486 by 1.25?Yes, indeed; but food for thought. Wouldn't this require a panel rated 800A; unless you can find a 600A, 100% rated breaker.
486 x 1.25 = 608A.
interesting, i have to admit. this stuff is now way over my head. hahaI'm glad you asked.
Check ANSI C84.1, Table 3-1, note d., also found in IEEE Std 141.
I find POCOs to be some of the worst offenders when it to using ANSI standard naming conventions.I'm glad you asked.
Check ANSI C84.1, Table 3-1, note d., also found in IEEE Std 141.
interesting, i have to admit. this stuff is now way over my head. haha
And I am not sure whether they are trying to still be obtuse, or just quick on their answers. Either you or the Engineer calculated the amps incorrectly. Phase A is 58,410/120 or 487 amps. The average amperage per phase is 161,850/208/1.73 that is VA divided by volts divided by the square root of 3.haha I just don't get why electricians never what to help each other. our trade is so cut throat its sad really...
I understand not wanting to teach non electricians something they shouldn't be doing but not helping your own brothers seems a shame.
Nobody can understand or know perfectly how to do everything, our trade is so broad.
Does the NEC require one follow this particular standard?I'm glad you asked.
Check ANSI C84.1, Table 3-1, note d., also found in IEEE Std 141.
NoDoes the NEC require one follow this particular standard?