I have a situation where we are feeding an electrical room with cables in tray under a raised access floor. We are feeding switchboards and UPS modules in this room. The area under the RAF is pressurized and used to cool the equipment from below via grills in the floor tiles. The HVAC units are located in the room, and none of the air is shared with any adjacent areas. All I can find in the code for this is Article 645 - Information Technology rooms. But this room is not an IT room, it is an electrical equipment room. Do the feeder cables need to be DP rated? Or can they be THHN/THWN CT rated cables(vertical flame test).
P.S. We have underfloor smoke detection wired to shunt trip the main feeds to the HVAC units in the event that smoke is detected.
Any advice is appreciated.
P.S. We have underfloor smoke detection wired to shunt trip the main feeds to the HVAC units in the event that smoke is detected.
Any advice is appreciated.