Drain Pipe Heat Trace

Status
Not open for further replies.

A-1Sparky

Senior Member
Location
Vermont
I've got a situation where heat trace was installed on drain pipes for an elevated podium walkway. It was installed about 12 years ago, and I've been told that it never worked properly. My question involves the design of such a system. There is no heat trace in the walkway itself, just the drain pipes. This walkway is about 16-18 feet wide and hundreds of feet long. Now, in order for this system to work properly, I contend that heat trace is needed in the walkway as well as on the drain pipes. I'm not 100% sure on that, hence my question. Can this work well the way it is designed now?
 
So this was a poor design from the get-go? The customer wants me to repair the heat trace, and is convinced that doing so would keep the walkway from icing up. I told him that in order for that to happen, they would need to install heat trace in the walkway as well. Does that sound about right?
 
I've got a situation where heat trace was installed on drain pipes for an elevated podium walkway. It was installed about 12 years ago, and I've been told that it never worked properly. My question involves the design of such a system. There is no heat trace in the walkway itself, just the drain pipes. This walkway is about 16-18 feet wide and hundreds of feet long. Now, in order for this system to work properly, I contend that heat trace is needed in the walkway as well as on the drain pipes. I'm not 100% sure on that, hence my question. Can this work well the way it is designed now?

Somewhat confused on the objective of the heat tracing here.

Heat tracing is commonly refered to as a means of preventing heat loss from an insulated piece of object.

It seems that the objective of the OP project is to:
  1. Keep ice off of the walkway
  2. make sure that the drainage does not freeze, plug up.
The above objective is not a heat tracing but a heating problem. The amount of heat required is magnitudes greater than a "heat tracing" would require.

Failed heaters would also need to be replaceable.
 
So this was a poor design from the get-go? The customer wants me to repair the heat trace, and is convinced that doing so would keep the walkway from icing up. I told him that in order for that to happen, they would need to install heat trace in the walkway as well. Does that sound about right?


Yes , That is only common sense.

It sounds like, as weressel said the heat tape was to prevent the drain from freezing. That is kind of important , too. Esspecially , well I'll just leave it at that.
 
It has been my experience with elevated platforms and walkways, to put heat trace cable on the drain traps and any exposed drain lines,along with a good quality insulation.

You put the heat trace cable on the trap because the drain trap is just that a trap. There is always (almost always) water in the traps. This creates a block to keep the sewer gases from escaping up through the drains. Should these traps freeze the drains do not drain and the water backs up on the surface which will create ice on the walk ways.

So Yes I can understand what your customer is asking. Ask the customer if he is concerned about frozen drains creating a back up which would freeze.
 
Yeah, that's my concern. He thinks that by replacing the heat trace on the drain pipes, that alone will be enough to keep the walkway from freezing up. I told him that it would definitely help, but he would also need to heat the walkway to prevent it from icing over. Thanks for the help, guys.
 