If it says 400AF & 300AT. The "F" is the frame and the "T" is trip? Which one indicated the size of the breaker? The frame I assume? For laboring purpsose I'm curious. Thanks.
400A breaker, just set up for 300A trip. Could be 300A CT's, CT tap, rating plug, etc...
So the frame is the breaker size
The frame is the frame size, depends on what the context of your question is. I don't get what laboring is.
400A is pretty small for a draw out breaker.
I don't think I have ever seen a 400AF draw out breaker in North American (ANSI) Metal Clad equipment with Power Circuit Breakers or Insulated Case Circuit Breakers, which is what I think Zog is thinking of.It is a drawout breaker.
The title of this thread is "Draw out breaker", so I assumed it was draw out![]()
"Laboring under a misconception"?... I would venture to guess that there is a good chance that this is a job that isn't a good match for him.
"Laboring under a misconception"?![]()
I don't think I have ever seen a 400AF draw out breaker in North American (ANSI) Metal Clad equipment with Power Circuit Breakers or Insulated Case Circuit Breakers, which is what I think Zog is thinking of.
Eaton - CH makes a 400A frame
So the frame is the breaker size
Good point. A basic old school thermal magnetic breaker would be limited to a fixed thermal, in this case 300a, and adjustable magnetic of 5-10 x the 300a or 1500-3000a. When supplied with an electronic trip all of the bells and whistles as you described are available. These features provide an means for coordination with other devices with similar features as well and integral ground fault which also has the ability to coordinate with devices with similar features.That is correct, a 400AF breaker is electrically and thermally designed to carry 400A continuously. The 300AT is indicative that it is equipped with a trip unit that will limit that continuous current to 300A. The trip unit most likely will also add some additional trip characteristics. The 300AT is indicative the Long time trip. Various Short time, Instantaneous ranges, Ground fault and delay adjustments are available to shape the tripping time/current curve of the breaker.
Do you sincerely believe that the OP understands what a draw out breaker is? If it has been listed on a BOM it is with almost all certainty a frame size and trip unit. Normally it will be fotpr an MCCBwith an IT which provide for the option of chance the trip to a 400at at a later date. Other wise the may specfy a a NIT breaker with a sealed trip such an C-H LBB3300 which would be a 400af with a sealed 300at trip unit.
Yes, on the long shot the it is a draw out ACB I would be looking for an actual spec and one line where the one line would show a draw out breaker and the specifications would include the features an options required.
As such a person who experience a reviewing BOMs should be able to quickly determine the requirement.
Oh, by the way, did you know that there is a draw out option for a 400a frame MCCB? A very expensive option which includes both moving and stationary parts.
There are also switchboards the MCCBs are mounted individually in their individual barriered compartments on use bus run backs to cunnect with bus as well as individually mounted MCCBs that have a plug on option using tulip connects and the basic stabs and jaws.
Yes, when I looked at the OP which the limited information as provided and no specifaction or one line provided 400af and 300at is a 400A frame breaker with a 300A trip is it installed. If it were to be more complicated than that there would have been a spec and one line included.
Just out of curiosity, what series? I couldn't find anything under 800AF in current products.Not quite understanding the need for the dissertation or all the speculation. I simply was letting Jraef know that there is at least one manufacturer that does make a 400AF draw out breaker.
Carry on......................
Just out of curiosity, what series? I couldn't find anything under 800AF in current products.
:rotflmao:Nothing current, looking on my shelf I have some FP-25's, ITE KB/KC's, Westinghouse DA, and Allis Chalmer LA-25A's that are all 400A draw out. Newest one of those was made in the late 50's.