Hello,
Where in the code book does it set the rules for drilling floor joists?
Running wires in basement ceiling and want to drill joists...
The joists are 2 x 10x 12
Thanks
It's called Boring and Notching.
If you don't find anything in the NEC look in the building code that applies to your project.
I have a PDF guide about boring and notching, but can not post it. PM me I will try to send it to you.
See if this helps
ry%3D480
If your question relates to a Commercial application, ...see Section 2308.9.10
& 2308.9.11 [ `12 IBC ] in to typical wood joists.........If cutting notching or
notching in to engineered joists, ...see the manufacturer' guidelines on their
limitations.
502.8 Drilling and notching. Structural floor members shall not be cut, bored or
notched in excess of the limitations specified in this section. See Figure 502.8.
502.8.1 Sawn lumber. Notches in solid lumber joists, rafters and beams shall
not exceed one-sixth of the depth of the member, shall not be longer than onethird
of the depth of the member and shall not be located in the middle onethird
of the span. Notches at the ends of the member shall not exceed onefourth
the depth of the member. The tension side of members 4 inches (102
mm) or greater in nominal thickness shall not be notched except at the ends of
the members. The diameter of holes bored or cut into members shall not
exceed one-third the depth of the member. Holes shall not be closer than 2
inches (51 mm) to the top or bottom of the member, or to any other hole
located in the member.
Where the member is also notched, the hole shall not
be closer than 2 inches (51 mm) to the notch.
Do not make this mistake. I have had many a friend call me only to have me give them the bad news.
Nothing like pulling all your wires out to have the carpenters sister all the joists.