The raceway articles require the raceway and associated fittings to be listed. In my opinion conduit bodies are fittings.don't think conduit bodies even need to be listed
I thought about that too, and decided they were not. So where do you stand on drilling holes? It voids the listing?The raceway articles require the raceway and associated fittings to be listed. In my opinion conduit bodies are fittings.
Nothing voids a listing...the listing only is for the product as it leaves the manufacturer. I have drilled and tapped holes for grounding screws, but never for mounting purposes.I thought about that too, and decided they were not. So where do you stand on drilling holes? It voids the listing?
Because it's a listed product or just generally because of 110.2?...........would need the approval of the AHJ.
Any time a product is modified in a manner not provided for in the installation instructions, listed or not, it is subject to approval, but that it true for everything, modified or not.Because it's a listed product or just generally because of 110.2?