Would they allow it using one of the Arlingtons with the removable sides?I doubt that any of the AHJs around here would allow that.
Would they allow it using one of the Arlingtons with the removable sides?I doubt that any of the AHJs around here would allow that.
I doubt that any of the AHJs around here would allow that.
IMHO it's wrong as for reasons previously stated. Very creative, but wrong. Why dont you use a pull box, that would have taken just bit longer.
(PS: your picture is gonna be on the bulliten board in my office, great conversation piece, no disrespect intended)
The installation would be in violation of 314.28(A)(2) for the required distance of 6 times the trade size (3/4") and the opposite wall of the conduit body.
I agree, that LB is not intended for that use.
Why does that matter?
Wouldn't using or applying an item for purposes other than it is approved for; be a violation of the listing itself? Example; using a ciruit breaker as a regular ON/OFF switch when it is not listed as such?
Would you mount terminal strips in an XJB, by drilling and tapping the wall?
As I pointed out.
ULs postion is it is up to the AHJ to determine if the modifications and use of the product are such that UL needs to do a field evaluation or the AHJ can certainly say no.
But in my personal opinon unless there is a safety issue I see no reason not to approve it.
I very rarely see specific labeling or instructions with enclosures or cabinets that say we may drill them at will yet we do that all the time with the blessing of the AHJ.
To reiterate my position, the AHJ certainly has the right to say no to this, but they are not required too, nor IMO should they.
It was somewhat of a trick question, but it illustrates that how easily important aspects of the listing is 'missed'.
An XJB refers to an Explosionproof junction box, and drilling and tapping the wall certainly would void the listing, as it weakens the wall of the box that is designed and tested to withstand an internal explosion, and no sane AHJ would override that.:roll::lol: