drop ceiling pendant outlet

I use a suspended-ceiling fan support with a 4" sq. box, a 3/4" to 1" single-gang plaster ring, a stainless blank plate with a 7/8" hole punched or hole-sawed, and a Kellums-type cable grip.
 
I use a suspended-ceiling fan support with a 4" sq. box, a 3/4" to 1" single-gang plaster ring, a stainless blank plate with a 7/8" hole punched or hole-sawed, and a Kellums-type cable grip.
Would this be ok for a suspended pendant. My worry would be the screws holding the cover. It might look bad but maybe use a stamped blank cover?
 
so attach a strain relief to the ceiling grid? I suppose that would be fine if I put it right below a tie supporting the grid.
I would put a chain or drop wire through the ceiling tile to support the hanger, and leave the grid as is. You cannot pass the cable through the grid ceiling, but hardware is fine, a threaded rod with an eye bolt could work as well. The spring on the hanger is important, if the drop gets pulled during use. along with a short loop of cable to allow it to move slightly with the spring.
I always leave a larger loop of cable for the drop to be relocated a short amount if their needs change later. You won't get any complaints if it's tied to the structure instead of the ceiling grid,
 
Code section?
314.23(h)(1) requires the cord or cable to be supported by approved means to protect the conductors against strain and if we choose to use a box equipped with a hub as a way to provide the proper box support the connection to the box must be with a cord attachment listed for use with a hub . Although a box with a hub is not “required” Idk how you’d provide the proper box support without using the hub otherwise you’d be relying on the locknut, and I’m not aware of a rule that requires the box in the ceiling to be equipped with a hub the cord just needs a form of strain relief
 

Attachments

  • IMG_1344.png
    IMG_1344.png
    302.4 KB · Views: 1
314.23(h)(1) requires the cord or cable to be supported by approved means to protect the conductors against strain and if we choose to use a box equipped with a hub as a way to provide the proper box support the connection to the box must be with a cord attachment listed for use with a hub . Although a box with a hub is not “required” Idk how you’d provide the proper box support without using the hub otherwise you’d be relying on the locknut, and I’m not aware of a rule that requires the box in the ceiling to be equipped with a hub the cord just needs a form of strain relief
5186-0 from www.hubbell.comCould probably use something like this and consider it a hub? or would that not be considered "a box with a hub"?
 