I have a 4square mounted to the ceiling, want to do a pendant for a #10/3 SO cord. Am I allowed to knock out the 1/2 inch hole to 3/4 on the cover ?
Just a short cord drop about 6 feet, the only 4 square covers seem to only have a 1/2 inch knockout, my cord needs 3/4.what type of pendant?
The K.O. set I have has a draw bolt that will stay centered in a 1/2" K.O. (7/8") hole.You might be better off starting with a blank cover and drilling a hole just large enough to clear the bolt of a 3/4 knockout punch. Otherwise it may be a struggle to keep the punch properly centered in a 1/2 hole if the bolt of your punch is significantly smaller. I think it can also produce a better result.
In fact Greenlee hydraulic punch sets come exactly that way, 1/2" KO punch is 3/8 draw screw and all the other sizes use a draw screw that centers close enough in that 1/2" KO hole.The K.O. set I have has a draw bolt that will stay centered in a 1/2" K.O. (7/8") hole.
Right. That's so you only have to drill a hole for the 3/8 screw, and use the 1/2" K.O. if you're going larger.In fact Greenlee hydraulic punch sets come exactly that way, 1/2" KO punch is 3/8 draw screw and all the other sizes use a draw screw that centers close enough in that 1/2" KO hole.
What wiring method is this 12/3 Bus Drop Cable? NEC 370.20(A)2 says Cablebus can't be smaller than 1/0I normally skip that process on that job, and use a blank plate and a holecutter. No layout or cross-hairs and punch centering required.
I also use bus drop cable, Kellems grip, and a sky-ty hanger for a stress relief.