OK, I thought I knew what I was doing (first mistake) but after reading a few other posts, now I'm not sure. We're putting in 12 drop cords in an office space. The plan was as follows:
Install 12 4 Square metalic boxes flush with the drop ceiling. These will be supported with unitstrut from the concrete ceiling above. We will install SO cord on twist-locks and use pendant rated boxes at the base. The plan was to use a strain relief (Amtec) attached to the 4 sq box.
The purpose of the drops is to service a group of tables in the center of the room. The tables are not moved real frequently, but the owner wants to have the option of moving them around somewhat.
Does this comply with NEC? Specifically 400.7 and 400.8. I thought it did, but in other posts some have felt that it is a violation of 400.8(4) because the strain reliev attaches the cord to the building. I always thought that section was referring to attachment to the building such as stapling it along a wall. I can't imagine why it would be a violation to attach a strain relief. Any thoughts on this fine point or any other part of the installation?
Thanks
Install 12 4 Square metalic boxes flush with the drop ceiling. These will be supported with unitstrut from the concrete ceiling above. We will install SO cord on twist-locks and use pendant rated boxes at the base. The plan was to use a strain relief (Amtec) attached to the 4 sq box.
The purpose of the drops is to service a group of tables in the center of the room. The tables are not moved real frequently, but the owner wants to have the option of moving them around somewhat.
Does this comply with NEC? Specifically 400.7 and 400.8. I thought it did, but in other posts some have felt that it is a violation of 400.8(4) because the strain reliev attaches the cord to the building. I always thought that section was referring to attachment to the building such as stapling it along a wall. I can't imagine why it would be a violation to attach a strain relief. Any thoughts on this fine point or any other part of the installation?