Drop Cord

Status
Not open for further replies.

Kthomas

New member
I have to install a cord drop( so type)from a concrete ceiling and with an oultet at the end 7ft above the floor. I have to pass thru a suspended ceilng ( lay in grids ) how can I make this legal?
 
Re: Drop Cord

Why does it "have to be" SO cord through that air space?

Could you possibly run a conduit(or similar) from the concrete ceiling to a box mounted to the grid and secured back up to the deck?

Could you possibly create a 2x2 opening in the ceiling, frame and sheetrock, and then run out of the deck box?

If that air space is the problem - eliminate it.
 
Re: Drop Cord

Take a look at Article 400.8(2)

400.8 Uses Not Permitted.
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted in this Code
(7) Where subject to physical damage
 
Re: Drop Cord

400.7 addresses ALLOWED uses.

I generally frown of using cords, but sometimes it is needed: ie, the lifts at your local auto shop; slicing and mixing machines at a cheese manufacturer(400.7(A)(8) ~ 2002).
Yes, these are places I worked in - either ends of the spectrum ~ auto shop=general filth/cheese production=general cleaniness.

EDIT:

I guess the OP will have to give us some more info on what's on the end of the cord ;)

[ October 24, 2005, 03:32 PM: Message edited by: celtic ]
 
Re: Drop Cord

how about running conduit down to the ceiling and installing a jbox on the bottom of the ceiling and starting the cord there. pull wire down to the jbox. then the cord is not passing through the ceiling, nor is it in the air space above the ceiling.
 
Re: Drop Cord

If damage to the drop ceiling is a concern, you could cut a 2' x 4' 5/8" plywood to fit into the tile opening, screw it to the t-bar real well, support the wood with rod if necessary, and then screw your j-box to the underside of the wood. Now a hard tug on the cord won't bring down the drop ceiling.
 