During a renovation I was told by the inspector that the 2x4 fluorescent fixtures installed in the drop ceiling had to be independently supported with tie wire or chain to the building joists above. I have not been able to find this in the code anywhere. Has anyone heard of this or am i just an idiot:-?
 
It is not an NEC issue, 410.16 is all that needs to be done for NEC compliance.

This would be a building code, it may have to do with the particular building design or seismic zoning.

Roger
 
I agree with Roger.

This requirement comes from the building code and is tied into seismic requirements for your area.

Chris
 
stpaul186

stpaul186

i am providing this link for informational purposes, you will want to check your local codes, city, county, state, etc. Further i have not used nor am i recommending this product. caveat emptor / buyer beware
 