Hello, I'm looking for help selecting a drum switch for a motor and have a few questions about it.

Motor: WEG W22 single phase (cat ID 00318ES1B184TC-W22) - 3 HP, 115/208-230 V

When looking into drum switches, most have a HP rating of 1.5 @ 115V and 3 @ 230V. In my case, I will be plugging this motor/switch into a typical 120V outlet. The data sheet for the motor gives a output of 3 HP with a rated voltage of 115/208-230 V. Should I assume the 3 HP output from the data sheet is at 230V and less for 115V? Or should I be looking for a drum switch rated for 3 HP @ 115V? Would there be any issue with drum switch with a lower HP rating than motor output?

Drum switch in mind:
Drum Switch
 
Hello, I'm looking for help selecting a drum switch for a motor and have a few questions about it.

Motor: WEG W22 single phase (cat ID 00318ES1B184TC-W22) - 3 HP, 115/208-230 V

When looking into drum switches, most have a HP rating of 1.5 @ 115V and 3 @ 230V. In my case, I will be plugging this motor/switch into a typical 120V outlet. The data sheet for the motor gives a output of 3 HP with a rated voltage of 115/208-230 V. Should I assume the 3 HP output from the data sheet is at 230V and less for 115V? Or should I be looking for a drum switch rated for 3 HP @ 115V? Would there be any issue with drum switch with a lower HP rating than motor output?

Drum switch in mind:
Drum Switch
Don't want motor starter and contactor instead drum switch?
 
Don't want motor starter and contactor instead drum switch?
Sorry, not completely familiar but do you have a link to a starter/contractor you could share?

I was planning to couple this motor to a gearbox/oil pump to transfer oil in/out of barrels and was envisioning wiring in a drum switch to control the direction. If you believe a starter/contractor may be a better route, please advise, I’m just not too familiar with setting those up or for my application.
 
Last edited:
Something like this, and you would need an overload block if the motor does not have overload protection built in. You would also need a control switch station.
 

Attachments

  • IMG_3279.png
    IMG_3279.png
    88.8 KB · Views: 6
Sorry, not completely familiar but do you have a link to a starter/contractor you could share?

I was planning to couple this motor to a gearbox/oil pump to transfer oil in/out of barrels and was envisioning wiring in a drum switch to control the direction. If you believe a starter/contractor may be a better route, please advise, I’m just not too familiar with setting those up or for my application.
Drum switch 3 hp, 115V may not available in market
Instead, use two magnetic contactors, forward and reversing, low rated drum switch in contactors coils circuits
Provide ocpd upstream
 