The schematic from post #31 shows a relay. A schematic does not always show physical location and/or what a device is.
I have assumed that the Heat Trace is a commericial box with an internal relay with some kind of contact terminating on a terminal pair for connection to external equipment. That would mean the relay is not easily replaced.
On to contact ratings. As a random sample of a small PC board mount relay see:
http://catalog.tycoelectronics.com/catalog/menu/en/16453?BML=10576,16354
http://catalog.tycoelectronics.com/catalog/feat/en/c/16656?BML=10576,16354,16453
http://catalog.tycoelectronics.com/...109941,109949,109950,109951,109947,109948^N~1
Look at the contact voltage ratings. Why would this be unsatisfactory to switch a low current resistive load at 120 V AC?
This one has higher breakdown voltage ratings:
http://catalog.tycoelectronics.com/...109941,109949,109950,109951,109947,109948^N~1
If one wants to have lower voltages at the Heat Trace for safety reasons, then the added relay at the PLC makes sense.
At the PLC input board do you really supply a contact closure, or do you apply a voltage signal? Does the PLC have any 24 V DC inputs?
.
The schematic from post #31 shows a relay. A schematic does not always show physical location and/or what a device is.
I have assumed that the Heat Trace is a commericial box with an internal relay with some kind of contact terminating on a terminal pair for connection to external equipment. That would mean the relay is not easily replaced.
On to contact ratings. As a random sample of a small PC board mount relay see:
http://catalog.tycoelectronics.com/catalog/menu/en/16453?BML=10576,16354
http://catalog.tycoelectronics.com/catalog/feat/en/c/16656?BML=10576,16354,16453
http://catalog.tycoelectronics.com/...109941,109949,109950,109951,109947,109948^N~1
Look at the contact voltage ratings. Why would this be unsatisfactory to switch a low current resistive load at 120 V AC?
This one has higher breakdown voltage ratings:
http://catalog.tycoelectronics.com/...109941,109949,109950,109951,109947,109948^N~1
If one wants to have lower voltages at the Heat Trace for safety reasons, then the added relay at the PLC makes sense.
At the PLC input board do you really supply a contact closure, or do you apply a voltage signal? Does the PLC have any 24 V DC inputs?
.