mykeknauff
Member
- Location
- Redwood City, California
- Occupation
- Electrical Engineer
I'm looking to place a particular instrument/monitoring system in a junction box in a Class 1 Div 2 area. The device has dry contacts and is not listed for use in class 1 division 2 environments. I'm thinking we may be able to use this anyway if we only use the device's 4-20mA output and leave the dry contacts disconnected. I see in the 2023 NEC section 501.105 (B)(2) that exception 2 allows for contacts in general purpose enclosures in non-incendive circuits. We would like to avoid putting these components in an explosion proof or purged enclosure. My interpretation is that leaving these contacts open circuited would make this section of the device a non-incendive circuit, however I don't have a lot of experience with classified areas so was hoping for a second opinion.