Consider a dry sprinkler system using vitrolic couplings connected to no compressor, pump, or any electrical component in a parking garage, using 250.104(B) does it require any bonding?
Roger
dry pipe with no compresser ? flame detectors, foam ? I give up, clue me in.
The theory behind the system is not the issue, the question is, if there is no water or chemicals in these pipes and there is nothing electrical connected to them, is there any requirement to bond them, there is nothing hidden in the question.
Roger
I think the point in nakulak's post is that a dry system is normally connected to an electrically power compressor.The theory behind the system is not the issue, the question is, if there is no water or chemicals in these pipes and there is nothing electrical connected to them, is there any requirement to bond them, there is nothing hidden in the question.
Roger
I think the point in nakulak's post is that a dry system is normally connected to an electrically power compressor.
so when theres a fire, someone has to go turn a big red handle that says "Rotate Clockwise In The Event Of Fire" on it?![]()
So what about the bonding requirement?
Roger
IMO, it is not "likely to become energized", so, no - bonding not necessary.
I don't think it is called a "dry system" then. I believe the correct term would be "manual deluge system". That being said, given the code wording change, a couple of cycles ago, from "may become energized" to "likely to become energized", I don't think the piping in question requires bonding and I don't think it would be "likely to become" energized even if there was a compressor.Normally that is true but, in this case I am told it is not, it is connected to a water main that must be opened manually so there is no compressor or pump involved, just an empty pipe system
Roger
I believe the correct term would be "manual deluge system".
Righty Tighty.so when theres a fire, someone has to go turn a big red handle that says "Rotate Clockwise In The Event Of Fire" on it?![]()