Dry sprinkler system and 250.104(B)

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Consider a dry sprinkler system using vitrolic couplings connected to no compressor, pump, or any electrical component in a parking garage, using 250.104(B) does it require any bonding?


Roger
 
Consider a dry sprinkler system using vitrolic couplings connected to no compressor, pump, or any electrical component in a parking garage, using 250.104(B) does it require any bonding?


Roger

IMO, it is not "likely to become energized", so, no - bonding not necessary.
 
dry pipe with no compresser ? flame detectors, foam ? I give up, clue me in.

The theory behind the system is not the issue, the question is, if there is no water or chemicals in these pipes and there is nothing electrical connected to them, is there any requirement to bond them, there is nothing hidden in the question.

Roger
 
The theory behind the system is not the issue, the question is, if there is no water or chemicals in these pipes and there is nothing electrical connected to them, is there any requirement to bond them, there is nothing hidden in the question.

Roger

I would think the contents of the pipe would be of no importance. We are bonding the metallic pipe to reduce the hazard of it becoming energized.
250.104(B) states "metal piping". In the case of most sprinkler systems, the with the non-conductive couplings it is impractical to bond them as you would need to bond each section.
 
The theory behind the system is not the issue, the question is, if there is no water or chemicals in these pipes and there is nothing electrical connected to them, is there any requirement to bond them, there is nothing hidden in the question.

Roger
I think the point in nakulak's post is that a dry system is normally connected to an electrically power compressor.
 
I think the point in nakulak's post is that a dry system is normally connected to an electrically power compressor.

Normally that is true but, in this case I am told it is not, it is connected to a water main that must be opened manually so there is no compressor or pump involved, just an empty pipe system

Roger
 
Last edited:
so when theres a fire, someone has to go turn a big red handle that says "Rotate Clockwise In The Event Of Fire" on it? :D
 
Normally that is true but, in this case I am told it is not, it is connected to a water main that must be opened manually so there is no compressor or pump involved, just an empty pipe system

Roger
I don't think it is called a "dry system" then. I believe the correct term would be "manual deluge system". That being said, given the code wording change, a couple of cycles ago, from "may become energized" to "likely to become energized", I don't think the piping in question requires bonding and I don't think it would be "likely to become" energized even if there was a compressor.
Note: CMP 5 is on record as saying these two terms mean exactly the same thing.
 
Unless terms have changed, my experience with a "dry system" is that a compressor keeps the system filled with air which keeps a valve closed to the water supply thus keeping the pipes from freezing. Once a sprinkler head is opened the air escapes allowing the valve to open and sending water into the system.

These systems are normally supplied by a fairly large underground water line, often iron which, IMHO, makes a good grounding electrode. I have heard refernce to a fire code that does not allow bonding to this main, but I have not actually seen such. In this area it is commonplace for that 1st section of sprinkler supply pipeing to be used as a grounding ekectrode per 250.52(A)(1)
 
I believe the correct term would be "manual deluge system".

Thanks for the clarification Don, that would be an accurate description of the system in question.

My position is that it is not required to be bonded either but, there is an inspector we have recently encountered that is not quite getting the gest of 250.104(B).