autotrans

Member
came across transformer install where it had been installed with both the primary and secondary conductors installed in the same raceway, I have not seen this before and could not find a code reference. Can you give any info on this method of installation.

[ January 09, 2005, 04:33 AM: Message edited by: autotrans ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: dry transformer install

The only code issues are conduit fill and conductor derating for more than 3 current carrying conductors.
Don
 