Dry transformer no-load consumption

Status
Not open for further replies.

mobo

Member
Location
MO USA
How much power will a 75 KVA dry transformer consume under a no-load condition on the secondary? Assume a primary voltage of single phase 480v and 240/120v secondary. I have heard anywhere from 3-6% of the rated current draw. Is this correct? My understanding is the secondary, of course, would draw no current but the primary would. Would appreciate any input on this.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
3-6% is pretty extreme. Most likely that’s someone’s guess based upon the impedance (%Z), falsely assuming that equates to losses.

I didn’t read all of that old thread, but in case it was missed, the magnetixing current you can read isn’t necessarily going to equate to a lot of power, because as magnetizing current it is going to be at an extremely low power factor, as in a .2PF in most cases. So although it may look like 2A at 480 V is 960VA, the actual Watts, which is what you PAY FOR, is only 960 x .2 = 192W. Over the course of a month of being energized 24/7, it’s only 140kWh, so about $15/ month for most people.
 

jumper

Senior Member
3-6% is pretty extreme. Most likely that’s someone’s guess based upon the impedance (%Z), falsely assuming that equates to losses.

I didn’t read all of that old thread, but in case it was missed, the magnetixing current you can read isn’t necessarily going to equate to a lot of power, because as magnetizing current it is going to be at an extremely low power factor, as in a .2PF in most cases. So although it may look like 2A at 480 V is 960VA, the actual Watts, which is what you PAY FOR, is only 960 x .2 = 192W. Over the course of a month of being energized 24/7, it’s only 140kWh, so about $15/ month for most people.

Why is the PF of the tranny so low under no load condition?
 
I think the no load losses can vary quite a bit depending on the design of the transformer. Very likely the newer the transformer, the lower the losses will be. .5% is the general figure given and I think in the ballpark for modern units. Pad mounts seem to have lower losses based on measurements I have taken. I have a 15 kva pad, 2400 to 120/240 and I measured it at 60 watts. I also have the same thing in a dry type and it is three times that. I have a real old control transformer, 10 kva same voltages, and that thing is a whopping 250-300 watts.
 

topgone

Senior Member
I think the no load losses can vary quite a bit depending on the design of the transformer. Very likely the newer the transformer, the lower the losses will be. .5% is the general figure given and I think in the ballpark for modern units. Pad mounts seem to have lower losses based on measurements I have taken. I have a 15 kva pad, 2400 to 120/240 and I measured it at 60 watts. I also have the same thing in a dry type and it is three times that. I have a real old control transformer, 10 kva same voltages, and that thing is a whopping 250-300 watts.

IMO, DOE's figure on no-load loss of a 75kVA Low Voltage Dry Transformer is about 120W (0.16%).
 
Last edited: