mwm1752
- Aspen, Colo
Call it a step if you want but as worded it only applies to stairway steps.
how may steps make a stairway?
More than one.how may steps make a stairway?
Yeah you made that point LOL. I posted when you did and it was mentioned above. So when does it become a stairway-- 2 step?
When it is a stairway.
I am sure the building code has a definition and surly part of that deffintion includes handrails
STAIR. A change in elevation, consisting of one or more risers.
STAIRWAY. One or more flights of stairs, either interior orexterior, with the necessary landings and platforms connectingthem to form a continuous and uninterrupted passage from onelevel to another within or attached to a building, porch or deck
George I took the liberty to post the pic as it is a interesting question. When does a step become a step-- hold long/wide/etc. View this larger with your browser to see details better. BTW, I can see Ryans response but without knowing the depth of the (step) I may challenge 110.26 but I suspect it is 36" or greater
I don't think that is what he is saying. He is saying that the area is not a stairwayIwire - Are you implying a platform need not meet clear space width & depth?
240.24(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway.
not in a building or structure so not a stairway, at least by this definition.
But by that definition, wouldn't a landing be considered part of the stairway, thus making a panel mounted over a stair landing a violation, regardless of whether or not space requirements are met?
I have not commented on that issue at all, yet.
My comments where only about code section 240.24(F) and how it relates to the picture Dennis posted for us here. https://forums.mikeholt.com/showthread.php?t=174325&p=1706764#post1706764
Now as far as 110.26 what specific section would you cite?
110.26 does not cover this, which was why 240.24(F) came into existence.
I cannot be sure but if those psot are 6x6 then the depth from the building out is maybe 20" -- the depth measured is infront of the panel which if my assumptions are somewhat correct is about 12" for the walkway disconnects. IMHO that is a step not a landing.
The far left disconnect working space appears compliant.
It is not a stairway so it does not apply.![]()
If it's in a commercial application the inspector is probably correct. Though only one hour is required for and exit stair well, but it could be two hour rated. Just because the contractor doesn't know doesn't mean the inspector doesn't, he may have been the one that originally inspected it.recently we had 100A circuit breaker installed in staircase. contactor advised us that inspector told him that c.b. should be in 2 hours rated enclosure. now I have doubts.
Sent from my Nexus 5 using Tapatalk
Even if it's not a step, I would still say that it infringes on your 3'. And just for clarification, a stair is a stair and a landing is a landing and there are definitions for both. When in doubt always look at the definitions and not necessarily the ones in the code book, the dictionary can be used and I believe that the one to use is talked about in the building code.I was going to ask about the same thing, how many steps needed before we have a stairway?
John, what specific code language do you see applying here?
In my opinion if that platform is a violation so are most concrete house keeping pads are.
Also if 110.26 was a factor there was no need for the fairly recent stairway rule in 240.