Hello and good day to all.
Am buying new electric clothes dryer and
wish to move to another location in the house.
I re-did the whole basement in EMT, so
I want to run 3/4" EMT from panel in basement
and up through the floor below the room where
the dryer will be located. It's about 40ft of pipe.
I don't have much residential wiring experience, so my question
is about the wire size. Seems number 10 THHN would work
but is it better to go up to 8AWG instead?
What would you guys normally run?
Thank you for your time.