isnt that a max load table?
No, Table 210.21(B)(3) is not Table 210.21(B)(2).
Different tables, different goals.
Table 210.21(B)(3) prohibits supplying a 50 amp receptacle from a 30 amp circuit.
Furthermore we cannot decide to use a 50 amp circuit to supply a typical residential dryer. Sections in article 422 will prohibit us from supplying the 24 amp dryer with a 50 amp circuit.