On a 220 V 3 prong dryer plug .... 2 hots and a ground ??
puckman said:Why Can You Ground The Neutral For A Dryer But Can,t For Most Any Other Installion ? Just A Though
paul said:Old house, get the three pronged pigtail and connect the neutral to the dryer chassis. Newer house (4-wire) use the 4 prong pigtail and seperate the ground and neutral wire as necessary.
allenwayne said:It was not an insulated grounded conductor but a bare grounding conductor.
Yes, but, i occasionally see a remodel where the sevice has been relocated. What once was a main breaker panel, is now a remote panel. Wouldn't you know, the neuts & grnds are not isolated & the bare ground wire to the range & dryer needs to be insulated at that point.infinity said:If this originates at the service equipment aren't they the same thing?
RUWired said:I think there is some confusion between se cable used for services and se cable used for dryers and ranges. The se cable used for services is used as a grounded conductor. The se cable used for dryer and ranges is an equipment ground. This was allowed to carry the neutral from the light bulb,but only with se cable.
Rick
RUWired said:The se cable used for dryer and ranges is an equipment ground. This was allowed to carry the neutral from the light bulb,but only with se cable.
Rick
RUWired said:O.K,So I am the one that was confused.I also looked in my older hand book and found the commentary stating that it was ok to use the neutral to ground the frames.Hard to believe the nec would'nt have said that is was ok to use the ground as a neutral for the small lamp.
Rick