I have a project where it has been proposed to use dual circuit lighting track with one circuit used for normal power lights and the other circuit used for emergency lights. Someone reviewing the project electrical drawings said this would violate NEC 700.10(B).
NEC 700.10(B)(2) says "Wiring supplied from two sources in exit or emergency luminaires" is permitted, so you can have both normal and emergency wiring entering a luminaire.
NEC 100 defines luminaire as "a complete lighting unit consisting of a light source such as a lamp or lamps, together with the parts designed to position the light source and connect it to the power supply. It may also include parts to protect the light source or the ballast or to distribute the light. A lampholder itself is not a luminaire."
Based on the definition of a luminaire, the track and the track heads together make up a luminaire. This is obvious but the reviewer doesn't buy it. He wants to know if the track and heads are UL listed for emergency operation, which doesn't make sense because, as far as I know, UL924 and 1008 don't apply to luminaires but to bypass and transfer equipment.
My questions are:
1. Are track and track heads ever UL listed for emergency operation?
2. Are there any NEC based arguments for track and track heads as a system to not be considered a luminaire?
Please provide answers/arguments based on the NEC or UL standards. I have been through too many discussions based on speculation.
Thanks.
NEC 700.10(B)(2) says "Wiring supplied from two sources in exit or emergency luminaires" is permitted, so you can have both normal and emergency wiring entering a luminaire.
NEC 100 defines luminaire as "a complete lighting unit consisting of a light source such as a lamp or lamps, together with the parts designed to position the light source and connect it to the power supply. It may also include parts to protect the light source or the ballast or to distribute the light. A lampholder itself is not a luminaire."
Based on the definition of a luminaire, the track and the track heads together make up a luminaire. This is obvious but the reviewer doesn't buy it. He wants to know if the track and heads are UL listed for emergency operation, which doesn't make sense because, as far as I know, UL924 and 1008 don't apply to luminaires but to bypass and transfer equipment.
My questions are:
1. Are track and track heads ever UL listed for emergency operation?
2. Are there any NEC based arguments for track and track heads as a system to not be considered a luminaire?
Please provide answers/arguments based on the NEC or UL standards. I have been through too many discussions based on speculation.
Thanks.