al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
If a "2 banger" is a nongrounding type receptacle, yes, it is exempted from the Tamper Resistant compliance. That is not new. That has been written in 406.12 in the 2014 NEC, as it is now.Unless i'm reading this wrong, my point is one can change out a 2 banger with a 2 banger non TP Al
~RJ~
Here's the thing RJ, 2017 NEC 406.4(D)(5) nongrounding type receptacle replacement does not relieve you from any of the rest of 406.4.
For me, and the work I get from time to time in dwellings with ungrounded wiring methods, with a worn out two wire receptacle, using a Dual Function AFCI GFCI TR device and labeling "No Equipment Ground" is the bee's knees.