Yes, you can find this in 230.90(A) exception 3.
Note that for 4/0 aluminum and when feeding other than just one individual dwelling the ampacity of the conductor is only 180 amps and not 200.
Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
So in this instance you are calling for a main panel then of only the four panel feeds to get the two to six circuits? Thus feeding each panel from its own breaker? This then would also mean the main breaker at this panel then simultaneously disconnects all four panels under it... Very interesting.
If it was done, due to the limits on number of breakers, you could not then do this in a series system, or would you if using through block panels? I mean, I know that you could do it using riser panels, the main cable being the feeder, and the panels thus getting the full voltage needed at each panel...
Still trying to get a handle on these bigger systems.