Duct Bank installations

Status
Not open for further replies.

phoenix68

Member
Location
US
Occupation
Student
According to NEC, does the duct bank run needs to be installed at a constant depth throughout the duct length? Or are there any provisions specifying certain length or percentage of total run can be deeper/shallower than the specified depth?

Can you please reference the article that specifies the same. Thanks for help.
 

tom baker

First Chief Moderator
Staff member
Burial depths are in table 300.5, which is cover to top. There are some special provisions for duct banks that I am not familiar with. No provision for percentages that you asked about.
 

phoenix68

Member
Location
US
Occupation
Student
Burial depths are in table 300.5, which is cover to top. There are some special provisions for duct banks that I am not familiar with. No provision for percentages that you asked about.
I see that 300.5 specifies the minimum depth required.

But for example, if I design ducts to be installed 36" deep for a total run of 150'. If during the run, for 10' length the duct is 48" below grade due to existing foundations. In such a case, while doing Neher Mcgrath calculations, should I be considering depth of ducts as 36" or 48"? I could not find anything related to this in NEC.
 