Duct smoke detector in return air shaft

Merry Christmas
Status
Not open for further replies.
Since the system serves more than one floor, and each air handler is larger than 2000 cfm, I would put a detector in each supply duct, 6-10 equivalent duct diameters from the air handler, and in the return from each floor, 6-10 equivalent duct diameters from where the duct leaves the floor.
 