Duct smoke detector in return air shaft

Status
Not open for further replies.
Since the system serves more than one floor, and each air handler is larger than 2000 cfm, I would put a detector in each supply duct, 6-10 equivalent duct diameters from the air handler, and in the return from each floor, 6-10 equivalent duct diameters from where the duct leaves the floor.
 