jonesy29847
Member
- Location
- Monroe, Michigan, Monroe
Thanks.
I am preparing to perform arc flash calculations for several manufacturing plants, typical incoming voltage is 480 3 ph, typically from 2500KVA transformers feed from the utility.
What if anything must I include from the utility side in my calculations?
Thank you in advance.
Fault current is not dependent on the load, it is a function of the available sources of current and the impedances connecting them.The thought here is most equipment should be very close in terms of fault current, like a Black and Decker drill, and a Milwaukee drill.
SCCR ratings from manufacturers deal with their ability to tolerate short circuit fault current. This rating has nothing to do with Arc Flash Incident Energy other than to determine if the equipment is 'overdutied' (applied beyond its limits).This is borne out by the fact that when our suppliers took the time to calculate the rms SCC Ratings are close.
I would guess the vast majority of our forum members spend the majority of their time involved with <600V systems.I get the impression that most of the members in this forum are MV and HV specialist.