I'd say your service conductors are in violation of 310.15 - I would say that you cannot use Table 310.15(B)(6) for the sizing of the service conductors (on the line side of the meters) because they do not serve an individual dwelling unit, they serve more than one dwelling unit. The conductors on the load side could use the Table, but the line side ones should technically be sized greater than the calculated service load, using Table 310.16.
I'd call it a minor violation, because if left to their own devices, the utility would likely have installed conductors smaller than that anyway.
I am also curious about your routing for the service entrance conductors between the meters and the panels. Are they through the slab?
(Not trying to pick on you, I've learned I had some bad habits before folks here pointed them out to me.

)