powerplay

Senior Member
In an old 1943 duplex, the main panel (without an disconnect switch) is located in the Fire separation wall, between the suites. i was wondering if there are any issues with the panel being located in the common wall anyone knows of?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
With a fire rated wall, any penetrations of that wall must maintain the fire resistance rating of the wall. That would mean that you most likely will have to wrap the cabinet with sheetrock or other approved material or methods that will maintain the fire resistance rating of the wall.