J jap Senior Member Occupation Electrician Nov 19, 2015 #1 Just saw a set of drawings where duplex receptacles were indicated to be controlled by a dimmer for floor lamps. Something just dont seem right about that. JAP>
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 19, 2015 #2 Generally not permitted unless you can comply with the new 2014 section 406.15.
al hildenbrand Senior Member Location Minnesota Occupation Electrical Contractor, Electrical Consultant, Electrical Engineer Nov 19, 2015 #3 jap said: Just saw a set of drawings where duplex receptacles were indicated to be controlled by a dimmer for floor lamps. Something just dont seem right about that. Click to expand... The key is in the equipment. The dimmer / receptacle have to be a listed combination. . . look at these Lutron application notes for how one manufacturer has put together a solution for what your drawings are calling out.
J jap Senior Member Occupation Electrician Nov 19, 2015 #4 That just goes to show they make something for everything if you just know about it. JAP>