Duty cycle and special motors
Brandon002
Tennessee
I want to be an electrician
Do you use the FLA conductors, OCPD and short circuit ground fault protection?
I did.
Now, in what context are you asking because your question isn’t clear?
I know that if it a normal motor
You would use FLC for conductors and short circuit/Ground fault protection
And for the OCPD you use the FLA
I was just wondering when it comes to the duty cycles , I was wondering if it the same when you’re sizing the OCPD and short circuit/ground fault protection
You would start with the type of motor and the table values at the end of art. 430
Use 430.52
That goes back to sizing for short circuit and ground fault protection
You would use 430.32