Duty cycle and special motors

I did.
Now, in what context are you asking because your question isn’t clear?

I know that if it a normal motor
You would use FLC for conductors and short circuit/Ground fault protection
And for the OCPD you use the FLA
I was just wondering when it comes to the duty cycles , I was wondering if it the same when you’re sizing the OCPD and short circuit/ground fault protection


Sent from my iPhone using Tapatalk
 
I know that if it a normal motor
You would use FLC for conductors
You would start with the type of motor and the table values at the end of art. 430
and short circuit/Ground fault protection
Use 430.52
And for the OCPD you use the FLA
That goes back to sizing for short circuit and ground fault protection
I was just wondering when it comes to the duty cycles , I was wondering if it the same when you’re sizing the OCPD and short circuit/ground fault protection


Sent from my iPhone using Tapatalk
You would use 430.32
 