Is there any code requirement to prevent Dw and disposols on seperate 15 amp Circuits? I have been doing them on seperate 20 amp circuits for 35 years but I am learning of much cheaper ways as of late.
Agreed.Jim W in Tampa said:Legal as long as the load is 15 amps or lower.
This, I'm not so sure about.Jim Walker said:And that disposal is a motor so it could even be on #14 and have a 20 amp breaker.
310.16 i believe as a motor it qualifies as 20 amp protection.georgestolz said:Agreed.
This, I'm not so sure about.
georgestolz said:If it were technically an "appliance" and not a "motor", then that would not be correct. "Appliances" are not listed in Table 240.4(G).
Since they are mentioned in Article 422, I tend to swing with the "appliance" train of thought, myself.
electricman2 said:Just got through with one. 14/3 to a split duplex, one switched for disposal.