Dwelling 120-Volt Smoke Detector Wiring

shortcircuit2

Senior Member
Location
South of Bawstin
I have a large 1-family dwelling with an existing hard-wired 120-volt smoke detector system. Now, a large addition to the existing dwelling will now require more that 12-smoke detectors which triggers the need for a fire alarm system.

Can the existing 14/3 Romex be used for a Class B SLC alarm circuit and install System Sensor smoke alarms via "pig-tailing" at each existing 14/3 hardwired outlet box without addressability? It appears this arrangement will also involve t-taps at some locations due to common existing 120-volt smoke detector wiring practices.

I searched forums but found now discussion of this situation.
 
I have a large 1-family dwelling with an existing hard-wired 120-volt smoke detector system. Now, a large addition to the existing dwelling will now require more that 12-smoke detectors which triggers the need for a fire alarm system.

Can the existing 14/3 Romex be used for a Class B SLC alarm circuit and install System Sensor smoke alarms via "pig-tailing" at each existing 14/3 hardwired outlet box without addressability? It appears this arrangement will also involve t-taps at some locations due to common existing 120-volt smoke detector wiring practices.

I searched forums but found now discussion of this situation.
It isn't clear what your intention is with the existing smoke alarms. They would have to all be replaced with the System Sensor smoke detectors. I assume you're going with a low-end Honeywell or similar panel and using the "SS" series detectors?
 
A 'Household Fire Alarm System' requires a Fire Alarm Control Unit (FACU), which would need to be listed as such under UL 864 Control Units and Accessories for Fire Alarm Systems.
A FACU for a simple residential system need not be a huge red panel in the basement, my NFPA 72 is out of date but it says a
Fire Alarm Control Unit (FACU) is defined as:
A component of the fire alarm system that receives signals from initiating devices or other fire alarm control units and processes these signals to determine part or all of the required fire alarm system output function(s).

If one or more of the smoke alarms is a FACU then it would be possible to soft upgrade a residential system, even zone it.
I have not done any product research on this but glancing at all the smart home smoke alarms on the market like 'Nest Protect', I would not be surprised if a residential product that can just replace one interconnected smoke alarm exists that would cover the minimum requirements for a residential FACU.
 
It isn't clear what your intention is with the existing smoke alarms. They would have to all be replaced with the System Sensor smoke detectors. I assume you're going with a low-end Honeywell or similar panel and using the "SS" series detectors?
Yes to be clear the existing 120-volt smoke alarms will be removed altogether, and the 120-volt interconnection capped off.

Use a low-end Honeywell alarm panel with SS series detectors with the detectors pigtail connected (T-tapped) using the red and black of the 14/3 romex which results in unsupervised detectors. The detectors will still trigger the alarm but if any detector is removed the alarm panel will not know. Connected similar as 120-volt smoke alarms where if any detector is removed the others still work.
 
Yes to be clear the existing 120-volt smoke alarms will be removed altogether, and the 120-volt interconnection capped off.

Use a low-end Honeywell alarm panel with SS series detectors with the detectors pigtail connected (T-tapped) using the red and black of the 14/3 romex which results in unsupervised detectors. The detectors will still trigger the alarm but if any detector is removed the alarm panel will not know. Connected similar as 120-volt smoke alarms where if any detector is removed the others still work.
If you use "SS" series detectors, these are addressable. If you pop one out, the panel will know. If you are using the 2WB conventional detectors, then you'll still know if someone removes one. They break the positive, and the detector has to be in place to maintain circuit continuity
 
What do you plan to do for sounders? Install sounder bases on each one?
You could, but now you have to pull power to the sounder base or jump up to the Siemens line with SLC loop powered sounder bases. It is starting to get expensive, because the other option is horn/strobes all over. But, given that the dwelling needs the extra detection, I doubt money is a huge object in this case.
 
You could, but now you have to pull power to the sounder base or jump up to the Siemens line with SLC loop powered sounder bases. It is starting to get expensive, because the other option is horn/strobes all over. But, given that the dwelling needs the extra detection, I doubt money is a huge object in this case.
Somehow the OP is going to need to get sounders in the bedrooms. My post was primarily to make sure they realized that.

Its been quite a few years but I have done non addressable systems in homes using smoke detectors with built in sounders and a reversing relay on the supply.
 