Is it compliant to wire a dwelling with 24 volts?
Is it compliant to wire a dwelling with 24 volts?
If NEC is the standard to comply with, all the outlets required by 210.52 are "125-volt, 15- and 20-ampere receptacle outlets".
210.63 is also 125 volt outlet when required.
good point. however does it say they actually have to be energized?
And one every 6/12 feet in majority of the rooms or 2/4 feet for kitchen counters as the general base - plus the rest of 210.52.Yes there are a few places that require 125V outlets as in a washing machine.
Let me be more direct--How do you think art. 710 affects the requirements in art. 210? Chapters 1-4 can be overridden by chapters 5-8
Yes there are a few places that require 125V outlets as in a washing machine.
Let me be more direct--How do you think art. 710 affects the requirements in art. 210? Chapters 1-4 can be overridden by chapters 5-8
Then I would say it's compliant in the sense that it isn't non-compliant.
Biggest issue is that it takes five times the current to deliver the same power.
So the question was asked in reference to a small cabin. It just seems like it can't be legit to me. The NEC makes such a big deal about wiring for all possibilities (spacing of receptacles, etc) that the 24v seems to negate it all.
I understand 710 coming into play but I just don't see how art. 210 can be basically ignored. If the stand alone system is 120v then I would have no issue but it just doesn't seem right to me
So the question was asked in reference to a small cabin. It just seems like it can't be legit to me. The NEC makes such a big deal about wiring for all possibilities (spacing of receptacles, etc) that the 24v seems to negate it all.
I understand 710 coming into play but I just don't see how art. 210 can be basically ignored. If the stand alone system is 120v then I would have no issue but it just doesn't seem right to me
Even if code compliant it may not be a very practical proposition.Only 24volts
Even if code compliant it may not be a very practical proposition.
Could you run an electric cooker, washing machine, clothes dryer, etc on a 24V supply?