And that comes back to what is the standard that must be met. If it is to be the NEC, and it does meet the NEC definition of a dwelling unit, 210.52 is a major hurdle to overcome if you don't have 120 volts in your supply system.I agree with these good points. However if they want insurance on the structure the AHJ may not just be the local building official but also the insurance co. I would focus on 90.1(A) and (B) the job of the NEC is not to select a voltage or system other than for practical safeguarding of persons and property.
The issue of 'Additional dwelling units' (ADU), 'Tiny Homes', Cabins, Yurts whatever they call it. I'd say 'small dwelling unit' it is upon us (the NEC).
I would be careful to go by the NEC definition of a dwelling unit "Dwelling Unit. A single unit, providing complete and inde-
pendent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation."
If its a hunting cabin with a detached outhouse for sanitation you dont have a dwelling unit.
I'd say article 230 is your minimum design requirement IF your using standard systems. And if you dont have voltage's recognized by NEC 220.5 and they are equal to or lower than the limits in 210.6 (it does not specify AC so DC is included)
And if our 24V (AC or DC) dwelling is a dwelling unit per NEC
I would look at article 411, and the historical article 720 that used to cover such rural 32V Delco systems in the days before grid service.
http://www.doctordelco.com/Dr._Delco/Delco-Light/Delco-Light.html
We could also pretend there were wheels on it and inspect it as a 'Recreational Vehicle' ART 551. And if there was no desire to supply 120V or 240V appliances in the future lots of that would not apply. But that's where I would go.
just my two cents
Cheers
Similar question has come up here before - can't remember how long ago it has been, but was regarding wiring a dwelling in accordance with NEC in a country where typical utilization voltage is 240 volt two wire. This was the same problem with that install - how do you comply with all the required receptacles by NEC that are supposed to be 125 volts?