Dwelling Load Calculation

Status
Not open for further replies.

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
I would look at the optional calculation in 220.82 for each dwelling unit, and in 220.84 for the total building.

I used the Method 220.82, but I don't think I am getting the correct incoming service.

For Single Phase I got 911 AMP and for Three Phase I got 527 AMP.


I also attached my updated Standard Calculation for Single and Three Phase.

Optional Calculation.jpg Single Phase Calculation.jpg Three Phase Calculation.jpg
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
Your total lighting and small appliance load is wrong on the optional method. That's why your total load is low.

Thanks for noticing that. I updated the Optional Calculation and now I get
For Single Phase I got 1021 AMP and for Three Phase I got 590 AMP.

I notice I made the same mistake for Standard and Three Phase as well, so would I use the amount of 3,856 VA which used the demand Factor of 3000 VA @ 100% and 35% after.


So for each apartment feeder, I will need a minimum of 120 AMPS based on Standard Calculation and optional comes out to 134 AMPS

Optional Calculation.jpg
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Thanks for noticing that. I updated the Optional Calculation and now I get
For Single Phase I got 1021 AMP and for Three Phase I got 590 AMP.

I notice I made the same mistake for Standard and Three Phase as well, so would I use the amount of 3,856 VA which used the demand Factor of 3000 VA @ 100% and 35% after.


So for each apartment feeder, I will need a minimum of 120 AMPS based on Standard Calculation and optional comes out to 134 AMPS

View attachment 22615

I think the 220.82 optional calculation for each apartment feeder would come out around 102 Amps.
 